Find references on generators and standby power for data centres. Review publications covering capacity selection, load response, fuel, emissions and operation, with bibliographic details and links to original sources.

Key numbers

Values hold under the conditions stated in each source. Read the cited page before using one in your project.

QuantityValueConditionSource
Local fuel tank per generator set (minimum)24 hoursWhere the seven-day fuel relies on deliveries, at full-load consumptionU.S. DoD (UFC), 2023 · p. 16
Load transfer time of an emergency-system ATS10 secondsNEC emergency systems; after loss of normal powerFEMA, 2014 · p. 19
Frequency deviation on a 100% load step (G2)-10%-7% for class G3U.S. DoD (UFC), 2023 · p. 23
Annual operating hours of the emergency standby rating200 operating hoursPrime ratings allow 10% overload for 1 hour in 12U.S. DoD (UFC), 2023 · p. 21
Maximum average load factor on a prime rating70%No hour limit; applied to the prime ratingU.S. DoD (UFC), 2023 · p. 28
Minimum loading to avoid wet stacking30%Of the generator ratingConsulting-Specifying Engineer, 2026 · Generator power

Design checklist

  1. Avoid generators sized beyond twice the current load and keep continuous loading at 30% or more of rated capacity. (FEMA, 2014)
  2. Record the generator EPSS class (fuel runtime), type (start time) and level. (NFPA, 2025)
  3. Set fuel to seven days of mission-load consumption; if relying on delivery, provide a 24-hour local tank per generator at full-load consumption. (U.S. DoD (UFC), 2023)
  4. For Tier III/IV targets, accept only generator ratings flagged 'continuous' or unlimited-hours during sizing. (Uptime Institute, 2018)
  5. Choose the generator multiplier (1.3 or 3.0) according to the UPS input THDi and power factor. (Schneider Electric, 2011)

Start with these sources

TM 5-698-5 Survey of Reliability and Availability Information for Power Distribution, Power Generation, and Heating, Ventilating and Air Conditioning (HVAC) Components for Commercial, Industrial, and Utility Installations (22 July 2006)

Headquarters, Department of the Army (U.S. Army Corps of Engineers PREP), 2006, Report

Describes how the U.S. Army Corps of Engineers Power Reliability Enhancement Program (PREP) collected field reliability data for more than 200 power and HVAC components. The database in Appendix B…

Report

2006

PDF

Tier Standard: Topology

Uptime Institute, 2018, Guide or technical publication

The normative Uptime document that defines the four Tier classifications through redundant capacity components and distribution paths. Its widely cited generator and fuel-storage provisions drive…

Guide or technical publication

2018

Read at publisher (opens in a new tab)

Related standards and regulations

Calculators and product

Power design in SoSo CAD

Calculate supply paths, equipment loads and UPS failure scenarios as part of the design.

Single-line diagram in the SoSo CAD power and capacity workspace

All documents in this topic

1–24 / 125

Regulations for Data Centers (Iowa DNR)

Iowa Department of Natural Resources, Year not stated, Guide or technical publication

Iowa Department of Natural Resources web guide: there is no single data-centre permit; withdrawals of 25,000 gallons or more per 24 hours, air, stormwater, wastewater and floodplain each need their…

Guide or technical publication

-

Read at publisher (opens in a new tab)