Airflow

Browse references on airflow management, aisle arrangements and rack inlet conditions. Investigate cooling distribution and air mixing alongside the measurement methods and modelling assumptions reported by each source.

Key numbers

Values hold under the conditions stated in each source. Read the cited page before using one in your project.

QuantityValueConditionSource
Fan energy reduction with containment20% to 25%DOE estimate; energy expense 5% to 10% lower in hot/cold aisle roomsU.S. Environmental Protection Agency (ENERGY STAR), 2026 · containment item
Raised-floor plenum static pressure0.05 in. of waterGives good perforated-tile airflow while limiting leakageLawrence Berkeley National Laboratory (Center of Expertise for Energy Efficiency in Data Centers) / U.S. DOE FEMP, 2020 · p. 42
Underfloor pressure for fan energy savings0.03 in.Can cut airflow and save fan energyLawrence Berkeley National Laboratory, 2014 · p. 17
Airflow required by IT equipment100 to 160 cfmPer kW; 47.2 to 75.5 L/sSchneider Electric, 2014 · Air distribution limitations

Design checklist

  1. Write cable management, blanking of rack openings, hot/cold aisle separation and containment, and at least 24 inches of clear raised-floor height into the design requirements for air management. (U.S. DOE FEMP / NREL, 2024)
  2. Compute required airflow with 100-160 cfm/kW (default 120 cfm/kW, about 56.6 L/s per kW). (Schneider Electric, 2014)
  3. Above 25 kW/rack, move to rack-based or liquid cooling. (Schneider Electric, 2012)
  4. With active tiles, always seal under-rack gaps; if left open, low pressure at the tile surface pulls hot air in under the rack and worsens the lower servers. (Frontiers in Energy Research (Frontiers Media SA), 2023)

Start with these sources

Related standards and regulations

Calculators and product

Cooling capacity in SoSo CAD

Check zone heat loads, installed capacity and the capacity left with the largest unit out, as part of the design.

Zone heat loads and capacity balance in the SoSo CAD cooling workspace