Racks

Sources on rack layouts, power density and IT equipment interfaces. Review technical notes to understand how mechanical, electrical and cooling requirements meet at the rack level.

Key numbers

Values hold under the conditions stated in each source. Read the cited page before using one in your project.

QuantityValueConditionSource
Limit of room CRAH and aisle containment approaches20 kW per rackApproximate limit for air-side approachesOpen Compute Project Foundation, 2023 · p. 9
Recommended depth for a liquid-cooled rack1200 mmKeeps rear plumbing clear of power and network cablingOpen Compute Project Foundation, 2023 · p. 15
Raised-floor uniform load (acceptable)732 kg/m2For 500 kg racks; optimum 1221 kg/m2Open Compute Project Foundation, 2020 · p. 12
Maximum rack PDU loading (North America)80%20 A gives 16 A; European 16 A breakers are 100%-ratedSchneider Electric, 2024 · Step 3
Cold aisle width (acceptable)1200 mm (48 in)Optimum 1500 mm; hot aisle 900 mmOpen Compute Project Foundation, 2020 · p. 29

Design checklist

  1. Size rack feeds by option: two independent 60 A NEC or 63 A IEC circuits, protection suited to 40 kA available short-circuit current at the tap-box, and no PDU in between. (Open Compute Project Foundation, 2026)
  2. Specify average and peak kW per rack for each row or zone; verify the source's peak-to-average assumption of 2 against project loads. (Schneider Electric, 2014)
  3. If any zone in a legacy room averages above 5 kW/rack, suggest a row-based pod. (Schneider Electric, 2012)
  4. For racks above about 70 kW, state that air cooling is insufficient and require a liquid-cooling path. (KPMG Türkiye, 2025)

Start with these sources

Open Rack V3 HPR V2 72kW Power Shelf, Rev 1.0.0 (June 12, 2026)

Open Compute Project Foundation, 2026, Guide or technical publication

The 1 OU power shelf for the High Power Rack (HPR) V2 houses six 12 kW PSUs, delivers 60 kW with N+1 redundancy and distributes 48-50 V DC over the rack busbar.

Guide or technical publication

2026

PDF

Related standards and regulations

Calculators and product

Data centre layout in SoSo CAD

Design rack layout, power supplies and cooling zones within the same project.

Racks and infrastructure equipment on a SoSo CAD floor plan

All documents in this topic

1–24 / 277

Energy Efficiency of Servers

IEA 4E EDNA, 2025, Guide or technical publication

The April 2025 IEA 4E EDNA study examines how server efficiency developed over the past decade: compound annual growth of 26% for general-purpose servers, 49% for accelerated computing chips and 47%…

Guide or technical publication

2025

Read at publisher (opens in a new tab)

All content and rights belong to the respective authors and publishers. SoSo CAD provides only the citation, its own summary and a link to the source, and is not responsible for the sources' content.

Keep your reading list current

Once a month: new library sources, changes to Turkish regulations and upcoming data centre events.