Topic

Liquid cooling

Find publications on direct-to-chip cooling, immersion and liquid loops. Investigate temperature conditions, facility interfaces and maintenance requirements for high-density data centre designs.

Key numbers

Values hold under the conditions stated in each source. Read the cited page before using one in your project.

QuantityValueConditionSource
Required operating temperature range (liquid loop)17-65 C2 C CDU approach and about 13 C delta-T; shipping range -40 to 75 COpen Compute Project Foundation, 2023 · p. 10
Rack density reachable with warm-water liquid cooling60 kW per rackThis value or moreNational Laboratory of the Rockies (formerly NREL), 2026 · page text
Share of heat captured directly to water98.3%Compute nodes only; 93.4% with the air-cooled power shelfNREL, 2019 · p. 6
Recommended design flow1.5 LPM/kWSaid to support most current chipsOpen Compute Project Foundation, 2024 · p. 19
TCS loop operating pressure140-450 kPaWith in-rack or row CDUs; facility CDUs may run higherOpen Compute Project Foundation, 2023 · p. 43
pH range of water-based coolant8.0-10.5Hardness below 30 ppm; turbidity below 5 NTUOpen Compute Project Foundation, 2023 · p. 8
PUE reduction against air cooling3% lower / 6% lowerFor cold plate and immersion respectivelyNature (Springer Science and Business Media LLC), 2025 · p. 5

Design checklist

  1. Arrange CDU redundancy so that fail-over valves feed rack groups from two different CDUs, letting the remaining units cool all racks when one CDU is lost or under maintenance. (U.S. DOE FEMP, 2021)
  2. For racks above about 70 kW, state that air cooling is insufficient and require a liquid-cooling path. (KPMG Türkiye, 2025)
  3. Plan thermal ride-through and a loss-of-flow response: redundant pumps, backup power, and extra loop volume nearest the IT. (Open Compute Project Foundation, 2024)
  4. Hold the chloride limit below 50 ppm wherever 304 stainless steel is used. (Open Compute Project Foundation, 2023)
  5. When TCS is 40 °C or higher, consider switching off adiabatic assist and show the water-versus-energy difference. (Schneider Electric, 2026)

Start with these sources

Related standards and regulations

Calculators and product

Cooling capacity in SoSo CAD

Check zone heat loads, installed capacity and the capacity left with the largest unit out, as part of the design.

Zone heat loads and capacity balance in the SoSo CAD cooling workspace

All documents in this topic

1–24 / 320

Developing a Mobile Cart for Datacenter Fluid Servicing, Revision 1.0

Open Compute Project Foundation, 2021, Guide or technical publication

An OCP document describing the requirements and design considerations for a mobile cart that charges, flushes, purges and drains cold-plate liquid-cooled racks at the rack position in the data hall.…

Guide or technical publication

2021

PDF

Duurzaam koelen van datacenters 2

Netherlands Enterprise Agency (RVO), 2022, Guide or technical publication

RVO's October 2022 brochure describes Dutch practice in free cooling, chilled water, F-gas-free refrigerants and direct liquid cooling through case studies, with PUE of 1.1 and below in several cases.

Guide or technical publication

2022

Read at publisher (opens in a new tab)

All content and rights belong to the respective authors and publishers. SoSo CAD provides only the citation, its own summary and a link to the source, and is not responsible for the sources' content.

Keep your reading list current

Once a month: new library sources, changes to Turkish regulations and upcoming data centre events.