Topic guide

Cooling

Explore technical publications on data centre cooling systems, thermal loads and operating conditions. Review air and liquid approaches, energy use and operational requirements within each source’s scope.

Sources
339
Downloadable PDFs
92
Years
2006–2026

All sources

145–168 / 339

Technical guideFree to read

TMMOB Makina Mühendisleri Odası (MMO) 2009

Energy efficiency in HVAC systems with dry-cooler free-cooling applications (Kuru Soğutuculu Doğal Soğutma Uygulamaları ile İklimlendirme Sistemlerinde Enerji Verimliliği)

Use the paper's mode thresholds (approach of about 2 C for partial and about 5 C for full free cooling) as defaults in a free-cooling-hours estimator, fed by city bin data for Turkish sites.

  • Targets 24/7 loads such as server rooms and data centres.
Technical guideFree to read

Uptime Institute Journal (Uptime Institute) 2021

New ASHRAE guidelines challenge efficiency drive

Tie the humidity control setting to the contamination class: allow the 70% RH upper limit only when coupon test results are entered and within limits.

  • The 5th edition includes a new high-density class.
Research paperPDF

Buildings (MDPI AG) 2023

Numerical Investigation of Thermal Performance with Adaptive Terminal Devices for Cold Aisle Containment in Data Centers

For hot-spot removal, before choosing lower supply temperature or higher airflow outright, compare the COP drop (3.2 to 2.6) and the energy difference (20.1% and 4.2%) with a rack-specific air distribution option.

  • A grid study at 260,000 to 1,340,000 cells showed results stabilising at about 560,000 cells.
Technical guideFree to read

Consulting-Specifying Engineer 2008

Outdoor air in data centers

In the tool's economizer studies, report hours below the humidity floor alongside energy savings, per climate.

  • NEBS levels 1-3 per SR-3580; level 3 applies to central-office equipment; key documents GR-63-CORE and GR-1089-CORE.
Research paperPDF

Buildings (MDPI AG) 2024

Performance and Applicability Analysis of Indirect Evaporative Cooling Units in Data Centers Across Various Humidity Regions

Assess an IEC unit by climate: natural cooling covered 97% of the year in a dry climate and 43% in a humid one; check the wet-bulb distribution (19 °C threshold) against project climate data.

  • Against packaged air-cooled DX units, IEC energy savings were 57.46% (Urumqi), 48.26% (Beijing) and 39.41% (Shanghai).
Research paperPDF

Frontiers in Energy Research (Frontiers Media SA) 2023

Performance evaluation and modeling of active tile in raised-floor data centers: An empirical study on the single rack

With active tiles, always seal under-rack gaps; if left open, low pressure at the tile surface pulls hot air in under the rack and worsens the lower servers.

  • CRACs were set to 21 °C but delivered 23 °C supply, and thermal load was about 65% of cooling capacity, so one CRAC was off.
White paperFree to read

Schneider Electric 2024

Power and Cooling Capacity Management for Data Centers

For every rack, row and upstream device store design maximum supply, design maximum demand (nameplate or as-configured) and measured actual where available; enforce supply >= demand at each hierarchy level including under N-1.

  • Safety margins are typically 10-20%, up to 30% or more with weak change control.

All content and rights belong to the respective authors and publishers. SoSo CAD provides only the citation, its own summary and a link to the source, and is not responsible for the sources' content.