The Green Grid 2008
WP#14 - The Green Grid Metrics: PUE/DCiE Detailed Analysis
In the PUE/DCiE calculator, cite this paper as historical provenance.
- Registration required; related standard ISO/IEC 30134-2.
Topic guide
Discover publications on data centre energy consumption, power demand and efficiency. Investigate measurement methods, operating conditions and improvement approaches through summaries and original references.
The Green Grid 2008
In the PUE/DCiE calculator, cite this paper as historical provenance.
Türkiye Elektrik Dağıtım A.Ş. (TEDAŞ) 2017
Default indoor data center transformers to cast-resin dry type; no oil pit is needed under the fire regulation.
Energy Efficient HPC Working Group / Lawrence Berkeley National Laboratory 2011
Implement this stack-up as a design check: from the site's 99.6% design wet and dry bulb plus per-component approaches, compute the achievable chiller-less supply temperature.
Monthly newsletter · free
Once a month: new library sources, changes to Turkish regulations and upcoming data centre events.
1–24 / 416
The Green Grid 2008
In the PUE/DCiE calculator, cite this paper as historical provenance.
Türkiye Elektrik Dağıtım A.Ş. (TEDAŞ) 2017
Default indoor data center transformers to cast-resin dry type; no oil pit is needed under the fire regulation.
Energy Efficient HPC Working Group / Lawrence Berkeley National Laboratory 2011
Implement this stack-up as a design check: from the site's 99.6% design wet and dry bulb plus per-component approaches, compute the achievable chiller-less supply temperature.
TELKODER - Telekomünikasyon Operatörleri Derneği 2021
In benchmarking views, use the quoted regional PUE (about 1.6) as a Turkish baseline.
U.S. Environmental Protection Agency (ENERGY STAR) 2026
Map each measure to an efficiency-check rule: missing containment, UPS in double-conversion only, no economizer, and so on.
European Commission JRC 2017
Store the best practice edition and version against each design so the compliance checker evaluates practices from the edition in force at design date (8.1.0 for 2017 projects).
European Commission JRC 2018
Keep the 2018 edition practices as a selectable compliance baseline for projects designed in 2018.
Data Center World / AFCOM 2026
Use AFCOM density figures (16 kW average; 50-70 kW for AI) as reference bands in the rack-density selector.
JLL 2026
In the cost module, use $/MW shell-and-core benchmarks (with year) as a sanity range for capex estimates, and show tenant fit-out separately.
Schneider Electric 2023
Model each meter point as a power-tree node with an aggregate flag so roll-ups never sum a parent and its child.
Caterpillar 2022
Store a fuel compatibility list (diesel, HVO/EN 15940) with an HVO derate percentage and an HVO-specific maximum block-load step in the catalog.
Open Compute Project Foundation 2024
Default the liquid cooling design wizard to an S30 (30 C) TCS supply with a 6 C CDU approach (24 C FWS) and 1.5 LPM per kW.
U.S. Environmental Protection Agency (ENERGY STAR) 2026
Use as quick-win recommendations in the operations module for small facilities.
Türkiye Büyük Millet Meclisi 2007
In the operations/energy module, compute annual energy in TEP (toe) from the energy model.
NVIDIA 2025
Add a single-ended 800 VDC distribution option to the electrical model, with rectifier blocks of ~1.5 MVA (LV) and up to 7.5 MVA (MV/SST) and the stated efficiencies.
arXiv preprint (National University of Singapore) 2025
For an operations or digital-twin module, use the feature list as a practical minimum sensor set for PUE prediction: outdoor dry/wet-bulb, IT power, UPS power, CRAC power/capacity/SCOP, coil temperatures and airflow.
Proceedings of the Twelfth ACM International Conference on Future Energy Systems (ACM) 2021
For geographic load shifting, consider locational marginal carbon emissions (lambda-CO2) as the signal instead of LMP or regional average carbon intensity; it gave the largest reduction (-1.44%).
IEEE Access (Institute of Electrical and Electronics Engineers (IEEE)) 2021
Set the number of spare PSUs/servers in a rack with a LOWP-style calculation from target service reliability and the load duration curve, avoiding unnecessary overprovisioning.
ACM/SPEC 2014
In the metering design module, offer Level 1/2/3 templates that place meters (for example upstream of PSUs/PDUs) and set the required coverage and sampling.
Schneider Electric 2015
Build the power-chain calculator as UPS(load) x wiring(load) x PSU(load), defaulting wiring to 1% loss at full load scaling with load squared.
IEEE Access (Institute of Electrical and Electronics Engineers (IEEE)) 2021
Define the failure state (loss of PDU power, loss of a rack, loss of service) explicitly before starting a reliability study and state it in the report.
Energies (MDPI AG) 2023
In UPS designs that only need bridging until the generator starts, evaluate a flywheel as a battery alternative, checking that a 15 s-15 min discharge range and a generator start under 10 s are adequate for the duty.
Energies (MDPI AG) 2021
In a central plant without a WSE, raise the chilled-water supply setpoint to about 11 °C; at 15-17 °C, CRAH fan energy increased total energy.
Electronics (MDPI AG) 2025
In efficiency reporting do not make PUE the only metric; knowing its weaknesses (manipulation, optimal-condition reporting, ignoring IT utilisation), complement it with WUE, CUE and IT-side metrics (SPUE, PpW, ITEE).