WP#14 - The Green Grid Metrics: PUE/DCiE Detailed Analysis
In the PUE/DCiE calculator, cite this paper as historical provenance.
- Registration required; related standard ISO/IEC 30134-2.
Topic guide
Explore publications on PUE and other data centre performance indicators. Before using a metric for comparison or design decisions, check its measurement boundaries, calculation method and required inputs against the original reference.
The Green Grid 2008
In the PUE/DCiE calculator, cite this paper as historical provenance.
Journal of Science Policy & Governance (Journal of Science Policy and Governance, Inc.) 2026
Give the sustainability panel at least four axes (PUE, CUE, WUE/WUEsource and a placeholder for IT productivity) and show them as a radar chart, so a low PUE never appears alone.
Uptime Institute 2018
Use as a historical data point for 2018 in a PUE and rack-density benchmark chart (PUE 1.58).
Monthly newsletter · free
Once a month: new library sources, changes to Turkish regulations and upcoming data centre events.
1–24 / 212
The Green Grid 2008
In the PUE/DCiE calculator, cite this paper as historical provenance.
Journal of Science Policy & Governance (Journal of Science Policy and Governance, Inc.) 2026
Give the sustainability panel at least four axes (PUE, CUE, WUE/WUEsource and a placeholder for IT productivity) and show them as a radar chart, so a low PUE never appears alone.
Uptime Institute 2018
Use as a historical data point for 2018 in a PUE and rack-density benchmark chart (PUE 1.58).
Schneider Electric 2023
Model each meter point as a power-tree node with an aggregate flag so roll-ups never sum a parent and its child.
Upsite Technologies blog 2014
Compute CCF for each room from running cooling capacity and IT load and show it as a KPI, with a warning when it is high (oversupply).
arXiv preprint (National University of Singapore) 2025
For an operations or digital-twin module, use the feature list as a practical minimum sensor set for PUE prediction: outdoor dry/wet-bulb, IT power, UPS power, CRAC power/capacity/SCOP, coil temperatures and airflow.
Frontiers in Sustainability (Frontiers Media SA) 2023
In data-centre siting, look beyond PUE to energy source (EnergyIn) and heat reuse (EnergyReuse), which PUE ignores.
ACM/SPEC 2014
In the metering design module, offer Level 1/2/3 templates that place meters (for example upstream of PSUs/PDUs) and set the required coverage and sampling.
Fluids (MDPI AG) 2026
Set WUE targets from the heat-rejection topology (dry, free-cooling, hybrid, evaporative) and not only the server-side cooling technology; WUE depends on the share of heat rejected by evaporation.
Electronics (MDPI AG) 2025
In efficiency reporting do not make PUE the only metric; knowing its weaknesses (manipulation, optimal-condition reporting, ignoring IT utilisation), complement it with WUE, CUE and IT-side metrics (SPUE, PpW, ITEE).
Applied Energy (Elsevier BV) 2025
In data-centre carbon accounting, state the method (Tier 1, 2, 3) and factor source (IPCC or national) when choosing a grid emission factor; simple methods can underestimate generation emissions by about 73%.
European Commission 2026
Translate PUE and WUE targets into A-G classes: class A needs a design PUE of 1.15 or below and WUE of 0.1 or below; the class D boundary is 1.5 and 0.6. Write the class target into the design specification.
ASHRAE 2020
In the CRAC catalogue, record rated capacity and efficiency (NSenCOP) on the basis of AHRI 1360 / ASHRAE 127 test conditions.
ASHRAE 2022
In the compliance calculator, compute annualised MLC and design ELC per segment (UPS, distribution, PDU) and compare them with climate-zone limits.
ASHRAE 2024
Use Book 2 (IT Equipment Power Trends) for default kW-per-rack growth projections.
Consulting-Specifying Engineer 2019
Implement the 90.4 MLC and ELC calculators with the correct test load points per UPS redundancy class (N/N+1 vs 2N).
arXiv preprint (cs.AI), Harvard T.H. Chan School of Public Health 2026
In fleet or facility energy estimation, use capacity × 8,760 × facility-load coefficient (0.48-0.70, central 0.58) and report the range (67.7-98.6 TWh) explicitly.
European Commission, DG ENER (AIT, Borderstep Institute, EY) 2025
Align the PUE target of new designs with the proposed MPS: design PUE below 1.3 and operational PUE below 1.4 in the first three years; for existing sites plan the path to below 1.5 by 2030.
TMMOB Makina Mühendisleri Odası (MMO) 2023
In the energy module, when on-site CHP/trigeneration is modelled, report PUE together with source-aware metrics (primary energy, CO2 and optionally exergy-based figures).
arXiv preprint (cs.CY; formatted for ACM e-Energy '26) 2026
In siting and community-acceptance files, present PUE, WUE and CUE together with regional water stress, grid headroom and verification maturity (L0-L4); back project commitments with contractual limits and independent metering (L2-L3).
European Commission, DG ENER 2026
Track this initiative as an upcoming rule pack; leave design headroom against likely MPS indicators (PUE, WUE, waste-heat reuse readiness, grid flexibility).
arXiv preprint (cs.SE), Google 2024
In allocating carbon to data-centre users, give idle power to whoever holds the resource allocation and share dynamic power by actual usage; because an idle server draws about 45% of peak power, the idle share is large.
ASHRAE 2022
In site comparison, compute both site WUE and source (grid) water using a regional EWIF, and optionally a scarcity-weighted index.
iMasons Climate Accord (Infrastructure Masons) 2025
Add embodied-carbon fields (kgCO2e; data source: EPD / TM65 / spend-based) to catalogue items and roll them up per design, reporting the share from supplier-specific EPDs.