White paperFree to read

Schneider Electric 2021

Rack Powering Options for High Density

In the rack power module, catalogue whip types, compute kW per whip as V x A x sqrt3 x 0.8 (three-phase) or V x A x 0.8 (single-phase), and default each rack to two three-phase whips (A/B).

  • Rack PDUs should be loaded to no more than 80% of rating.
White paperPDF

Open Compute Project Foundation 2023

White Paper: Guidelines to Rack Manifold Requirements and Qualification

Write MAWP with at least 3x burst pressure, the 17-65 C operating and -40 to 75 C shipping ranges and the 1.5 m/s velocity limit into the manifold specification; because the range is based on ASHRAE W45, ask suppliers for a higher rating if a warmer-water strategy is planned.

  • Shelf life is 5 years and service life is 10 years.
White paperPDF

Open Compute Project Foundation 2026

Whitepaper: Thermal Boundaries in AI Infrastructure - Matching cooling technologies to compute through the power inflection, Version 1.00 (October 2026)

Choose cooling architecture against target rack power and each method's usable envelope: a 45 kW air ceiling (60-80 kW with rear doors), 120-250 kW class cold-plate racks, and the paper's anchor values for announced 600 kW-class racks.

  • Practical air-cooled rack ceiling is taken as 45 kW, extendable to about 60-80 kW with rear-door heat exchangers.