The Green Grid 2012
WP#48 - Evaluation of Eco Mode in Uninterruptible Power Supply Systems
In the UPS module, model double-conversion and Eco/ESS modes with separate efficiency curves.
- Related standard: IEC 62040-3.
Topic guide
Explore publications on data centre electrical infrastructure, from power distribution and protection to supply architectures and capacity planning. Compare technical summaries, publication details and links to the original references.
265–288 / 358
The Green Grid 2012
In the UPS module, model double-conversion and Eco/ESS modes with separate efficiency curves.
The Green Grid 2012
In phased-build planning, support staged UPS and generator modules with efficiency at each load step.
The Green Grid 2013
Compare THDi and THDv against IEEE 519 limits at the PCC rather than demanding near-zero values.
The Green Grid 2015
Offer a reduced-conversion topology scenario.
The Green Grid 2016
Store PSU ride-through (ms) as a catalog field for IT equipment.
The Green Grid 2016
Catalog the ride-through time per PSU.
The Green Grid 2022
For EU sites, default server PSU efficiency to the Lot 9 (Regulation (EU) 2019/424) minimum.
The Green Grid 2023
Add a 480Y/277 V-to-rack option with 277 V PSUs and no PDU transformer to the electrical topology library.
Schneider Electric 2026
Add a distribution architecture option for AI halls: AC 415/240, 48 VDC busbar, 800 VDC sidecar, 800 VDC centralized.
Schneider Electric 2026
In the schedule estimator, default MV switchgear lead time to about 26-32 weeks (ETO)
BICSI 2024
Offer BICSI classes as an alternate standards profile alongside Uptime/TIA/EN, with an F1~Tier I/Rated-1/Class 1 ... F4~Tier IV/Rated-4/Class 4 table labelled 'conceptual equivalence only'
Telecommunications Industry Association 2024
In a 'TIA-942' standards profile, let users pick a rating per discipline (for example electrical Rated-3, mechanical Rated-3, telecom Rated-2)
Eaton 2016
Add a designLifeYears catalog parameter per equipment type, default to the range midpoint, and drive a TCO/refresh timeline from it.
U.S. DOE FEMP / NREL 2024
Weigh the supply air setpoint against server fan energy: raise it in small steps within the ASHRAE recommended range so the most demanding inlet nears 80 °F, only after air management is in place, and control to IT inlet temperature rather than return temperature.
Schneider Electric 2013
Use this paper as the template for the Design Basis form: target average kW per rack, peak kW per rack (default 2x average), density uncertainty (default 15%), managed power ratio (default 0.7) and reserve space (default 15%).
Schneider Electric 2017
Implement as the default heat-load calculator: Q = IT + (0.04 x UPS + 0.05 x IT) + (0.01 x UPS + 0.02 x IT) + 14.32 x area + 100 x people
Schneider Electric 2011
Use it as a quick-sizing calculator in novice mode: take IT kW, future kW, floor area, cooling type and UPS input type, and output service kW/A and generator kW, with the multipliers as editable defaults.
Open Compute Project Foundation 2020
Check the delivery route against rack height plus 0.5 m, door and corridor widths, and the lift capacity, before agreeing to host or design for Open Racks.
Schneider Electric 2011
When topology is 2N but some loads are single-corded, require a rack ATS per single-corded device by default.
Schneider Electric 2016
Offer N, isolated redundant, N+1, distributed redundant (catcher/STS), tri-redundant, 2N and 2(N+1) in the topology library, and label availability values as comparative rather than absolute.
Schneider Electric 2022
In the single-line builder, raise a warning when the transfer switch has 4 poles and the UPS neutral is not separately derived.
Vertiv 2017
In A/B (2N) racks keep each feed's design load at or below rating x 0.8 (80%-rated breaker) x 0.5; for single phase usable kW = V x I x 0.8 x 0.5.
Schneider Electric 2026
Add an OT-network section to the design: each monitored device class carries a protocol list and an IEC 62443 certification flag.
Open Compute Project Foundation 2026
For a new site, write the POI LVRT/HVRT envelope and the PFAPR requirement (90% within 2 s) as design criteria, and settle which voltage measurement (line-to-neutral or line-to-line) governs during protection coordination with the utility.
All content and rights belong to the respective authors and publishers. SoSo CAD provides only the citation, its own summary and a link to the source, and is not responsible for the sources' content.