High-Performance Computing Data Center Heat Capture and Reuse (ESIF)
In the heat-reuse module, support on-site end uses (low-temperature terminals, snow melt).
Topic guide
Find publications on direct-to-chip cooling, immersion and liquid loops. Investigate temperature conditions, facility interfaces and maintenance requirements for high-density data centre designs.
49–72 / 153
National Laboratory of the Rockies (formerly NREL) 2026
In the heat-reuse module, support on-site end uses (low-temperature terminals, snow melt).
National Laboratory of the Rockies (formerly NREL) 2026
Use as a reference case for warm-water DLC presets (supply about 24 C, return about 38 C).
Open Compute Project Foundation 2025
In CDU catalogue entries, distinguish single-phase and two-phase (refrigerant type, saturation temperature, facility-water supply temperature).
Danfoss 2024
In the liquid-cooling catalogue store coupling size, OCP compliance, maximum working pressure, flow coefficient/pressure drop, disconnect-under-pressure limit and wetted materials.
Consulting-Specifying Engineer 2021
Offer integrated-free-cooling chillers as a catalogue option with the free-cooling changeover ambient field.
Consulting-Specifying Engineer 2025
Liquid-loop design rules: check pipe velocity <= 2.1 m/s above 3 in. NPS and TCS supply >= dewpoint + 2 C, and flag incompatible wetted materials.
Leibniz Supercomputing Centre 2025
Let liquid-cooled design templates allow facility supply temperatures up to 45 C with dry-cooler-only heat rejection, and show the resulting PUE.
Huawei Digital Power 2025
Import RD 01-21 as parametric AI-hall templates (rack kW, racks per module, module kW, redundancy of fan walls/TMUs/towers, generator and transformer counts) and as golden test cases for capacity math.
Cundall (for Iceotope Technologies) 2021
Catalogue liquid-cooled IT and CDUs with ASHRAE W-class and supply temperature fields, and use these to decide whether compressor cooling can be omitted for the site climate.
Applied Thermal Engineering (Elsevier BV) 2025
In hybrid immersion/direct liquid cooling design, rank dielectric fluids by FOM1, but remember a high-FOM1 fluid can infiltrate the TIM of cold-plated CPUs and raise their temperature.
Open Compute Project Foundation 2025
Give immersion tank and server catalogue items a field-reliability reference (AFR), and use component-level AFRs in the reliability module rather than assuming immersion degrades availability.
IEEE 2012
In liquid-cooling energy calculations, account for glycol concentration (higher pumping power, lower heat transfer) and flow-rate set points, not just supply temperature.
Energies (MDPI AG) 2019
Consider a cabinet-level rear-door heat exchanger as an option that can raise heat dissipation by 56-67% over air cooling; compare oil or water coolant separately on leakage risk and maintenance.
Uptime Institute Journal 2026
Catalogue DLC loops with coolant type (PG25/DI), filtration rating (default 25 micron) and wetted materials.
STULZ 2024
Model the per-rack heat split (liquid %/air %); it drives both CDU and CRAH sizing.
STULZ 2025
Define rack templates per GPU generation with a default kW and liquid/air split, for example 85/15 at 130 kW and 100/0 at 600 kW.
STULZ 2025
In the CDU selection tool let users trade approach temperature against heat-exchanger area and TCS delta-T, with Cases 1-3 as validation fixtures.
Energy Efficient HPC Working Group 2013
In commissioning checklists the tool generates for liquid-cooled plants, include verification that instrumentation matches manufacturer specifications.
ASHRAE 2013
In the DLC data model, keep facility water (FWS) and technology cooling system (TCS) loops separate, with a CDU as the interface.
WSP 2026
For TCS loops, add coolant fields (demineralised water, PG percentage).
Open Compute Project Foundation 2021
Add mechanical, hydraulic, electrical and network inspection protocols and a recorded pressure-decay test to the delivery and commissioning plan for rack acceptance.
Data Center Knowledge 2026
Add a retrofit check comparing liquid-cooled rack weight (default up to about 3,000 lb / 1,360 kg) with the raised-floor rating.
STULZ 2026
In the liquid-cooling module size TCS flow at about 1.5 L/min/kW by default and store CDU approach temperature and external static pressure.
Open Compute Project Foundation 2024
Store CDU capacity in the catalogue using this rating basis (kW at 5 C ATD, 1.5 LPM/kW, head and FWS impedance) so units from different vendors can be compared, and derate when the design ATD or flow differs.