Humidity Control in Data Centers (March 8, 2017)

Write the humidity strategy around room dew point: set a wide dead band (about 16 °F to 59 °F dew point unless the IT owner agrees a higher lower limit) rather than a narrow RH band.

  • Class A1 equipment is known to function up to 90 °F and A4 up to 113 °F, although all classes share the same recommended range.
Technical guidePDF

U.S. DOE FEMP 2010

Operations & Maintenance Best Practices: A Guide to Achieving Operational Efficiency, Release 3.0 (August 2010)

Choose maintenance strategy by equipment criticality: predictive for critical equipment with random failures, preventive for equipment subject to wear, reactive for small non-critical items; build a master equipment list and priority matrix.

  • Boiler combustion tuning and related O&M can yield fuel savings of 2% to 20%.
Technical guideCitation

NREL 2017

Thermosyphon Cooler Hybrid System for Water Savings in an Energy-Efficient HPC Data Center: Modeling and Installation (NREL/CP-2C00-66690, February 2017)

Place a dry stage upstream of the tower and size it against the share of hours where warm return water exceeds dry-bulb temperature by enough margin, as the 9.4 °C transition point does here.

  • Building heat reuse peaks at 0.434 MW of a 0.910 MW load, leaving 0.496 MW to reject to atmosphere.
Technical guideCitation

NREL 2018

Thermosyphon Cooler Hybrid System for Water Savings in an Energy-Efficient HPC Data Center: Results (NREL/TP-2C00-72196, September 2018)

Check whether the warm return water from liquid cooling (here 84 °F after energy recovery) leaves enough temperature difference to ambient for a dry or hybrid stage, and size it against local dry-bulb hours.

  • First-year heat rejection: 10.5% building heat reuse, 42.5% thermosyphon and 47% cooling towers.