Water

Find references on data centre water consumption, cooling water and water efficiency. Investigate local conditions, measurement boundaries and the relationship between energy and water use through technical notes.

Sources
93
Downloadable PDFs
26
Years
2009–2026

All sources

49–72 / 93

Research paperPDF

Sustainability (MDPI AG) 2015

The Water Footprint of Data Centers

Compare HVAC options not only by on-site water use but by total water footprint including the grid's water intensity (WUEsource); the ranking can flip with the grid.

  • Outbound data traffic carries a water footprint of 1-205 litres per gigabyte; the high end is close to the 214 L footprint of 1 kg of tomatoes.
Research paperFree to read

Nature (Springer Science and Business Media LLC) 2025

Using life cycle assessment to drive innovation for sustainable cool clouds

Add a cooling-technology comparison calculator that computes annual energy as IT MW x load factor x PUE x 8760 and applies the paper's Table 3 deltas (PUE -3%/-6%, IT capacity +3%/+6%) and Table 4 savings ranges as tagged defaults.

  • Switching to 100% renewable electricity cut GHG by 85-90%, energy demand by 6-7% and blue water by 55-85%; server embodied carbon became more significant.
RegulationPDF

European Commission (Official Journal of the European Union) 2024

Commission Delegated Regulation (EU) 2024/1364 of 14 March 2024 on the first phase of the establishment of a common Union rating scheme for data centres

Build the metering architecture to the regulation: meters on every supply input for total energy (grid and back-up generator separately) and at every UPS output for IT energy, with a system that retains measurement point and device records for at least 10 years.

  • Data centre electricity demand is projected to reach 3.2% of total EU demand by 2030, a 28% increase over 2018.
White paperPDF

Open Compute Project Foundation 2024

Data Center Facility Sustainability Metrics (OCP Data Center Facility white paper, October 2, 2024)

Build the metering plan so that PUE can be reported at the highest category possible, with IT load measured at PDU or equipment input rather than the UPS output where feasible.

  • External reporting is annual (required) and quarterly on a trailing 12 months (recommended); internal tracking should be continuous or monthly.
White paperFree to read

Schneider Electric 2011

Economizer Modes of Data Center Cooling Systems

Compute economizer hours from hourly climate data (dry bulb and wet bulb) against the chosen supply setpoint and approach temperatures, and report partial and full economizer hours separately.

  • Cooling towers consume about 40 gpm per 1,000 tons of capacity (151.4 L/min).