Discover publications on data centre energy consumption, power demand and efficiency. Investigate measurement methods, operating conditions and improvement approaches through summaries and original references.

Sources
416
Downloadable PDFs
122
Years
2007–2026

All sources

313–336 / 416

Research paperFree to read

IEEE Transactions on Sustainable Computing (Institute of Electrical and Electronics Engineers (IEEE)) 2025

xPUE: Extending Power Usage Effectiveness Metrics for Cloud Infrastructures

Do not present facility PUE as the whole efficiency story: add an optional server-overhead factor (sPUE) to the energy model and show an 'effective PUE' = PUE x sPUE next to PUE.

  • Idle servers gave sPUE > 4; on a Dell R640 under rising CPU load the average sPUE was 3.1 and the lowest 2.7.
Research paperPDF

Sustainability (MDPI AG) 2025

Zero-Carbon Development in Data Centers Using Waste Heat Recovery Technology: A Systematic Review

In waste-heat use, first match technology to source temperature (heat pump 20-55 °C, absorption cooling 30-85 °C) and think of electricity, heat, cooling and storage together rather than a single technology.

  • Heat pumps for WHR are listed for source temperatures of 20-55 °C and absorption refrigeration for 30-85 °C.
Technical guidePDF

European Commission JRC 2025

2025 Best Practice Guidelines for the EU Code of Conduct on Data Centre Energy Efficiency (JRC141521, EUR 40267)

Design the facility to operate within the ASHRAE Class A2 allowable range and require A2 operation within warranty in IT procurement; plan separate environmental zones (practice 5.3.4) for legacy equipment.

  • IT equipment AC/DC power converters should be rated at 90% efficiency or better across expected load ranges.
Technical guidePDF

U.S. DOE FEMP / NREL 2024

Best Practices Guide for Energy-Efficient Data Center Design (Revised July 2024)

Weigh the supply air setpoint against server fan energy: raise it in small steps within the ASHRAE recommended range so the most demanding inlet nears 80 °F, only after air management is in place, and control to IT inlet temperature rather than return temperature.

  • Compute racks reached 60 kW in 2013, and recent liquid-cooled racks exceed 125 kW.
White paperFree to read

Schneider Electric 2011

Calculating Total Power Requirements for Data Centers

Use it as a quick-sizing calculator in novice mode: take IT kW, future kW, floor area, cooling type and UPS input type, and output service kW/A and generator kW, with the multipliers as editable defaults.

  • Actual IT power is roughly nameplate VA x 0.67.
RegulationPDF

European Commission (Official Journal of the European Union) 2024

Commission Delegated Regulation (EU) 2024/1364 of 14 March 2024 on the first phase of the establishment of a common Union rating scheme for data centres

Build the metering architecture to the regulation: meters on every supply input for total energy (grid and back-up generator separately) and at every UPS output for IT energy, with a system that retains measurement point and device records for at least 10 years.

  • Data centre electricity demand is projected to reach 3.2% of total EU demand by 2030, a 28% increase over 2018.