The Green Grid 2022
WP#85 - 230V Enterprise PSU Market-Ready Efficiency Study
For EU sites, default server PSU efficiency to the Lot 9 (Regulation (EU) 2019/424) minimum.
- Scope is 230 V enterprise power supply units.
Topic guide
Discover publications on data centre energy consumption, power demand and efficiency. Investigate measurement methods, operating conditions and improvement approaches through summaries and original references.
313–336 / 416
The Green Grid 2022
For EU sites, default server PSU efficiency to the Lot 9 (Regulation (EU) 2019/424) minimum.
The Green Grid 2022
In the storage catalog, capture power per capacity or performance from SNIA Emerald-style test data rather than nameplate.
The Green Grid 2023
Add a 480Y/277 V-to-rack option with 277 V PSUs and no PDU transformer to the electrical topology library.
IEEE Transactions on Sustainable Computing (Institute of Electrical and Electronics Engineers (IEEE)) 2025
Do not present facility PUE as the whole efficiency story: add an optional server-overhead factor (sPUE) to the energy model and show an 'effective PUE' = PUE x sPUE next to PUE.
Eaton 2021
In the asset/lifecycle module store the installation year per UPS and battery, and project replacement dates from the component table defaults.
TMMOB Makina Mühendisleri Odası (MMO) 2007
Warn when IT and comfort loads share one UPS or one chilled-water primary loop, since that blocks independent temperature reset and free cooling.
Sustainability (MDPI AG) 2025
In waste-heat use, first match technology to source temperature (heat pump 20-55 °C, absorption cooling 30-85 °C) and think of electricity, heat, cooling and storage together rather than a single technology.
Schneider Electric 2025
In the sustainability panel compute operational CO2e = IT MWh x PUE x grid EF, with a grid-EF catalog by country/region (default US 454 kg CO2e/MWh incl. upstream) and a renewable-PPA toggle.
Schneider Electric 2025
Default TCS supply to 40 C for liquid-cooled designs; warn below 30 C (efficiency loss) and above 45 C (server spec limit).
Lawrence Berkeley National Laboratory 2024
Take AI rack and node power assumptions (3.4 to 12.2 kW per 8-GPU server, 20% idle) as a cross-check on IT load models, not as a substitute for vendor data.
European Commission JRC 2025
Design the facility to operate within the ASHRAE Class A2 allowable range and require A2 operation within warranty in IT procurement; plan separate environmental zones (practice 5.3.4) for legacy equipment.
Google 2020
Add an "hourly CFE potential" score per candidate grid (grid CFE% plus PPA options) to site selection, beside annual renewable %.
European Commission, DG Energy 2025
Compare your design PUE target with the real EU spread: 1.21 on average above 10 MW, 1.55 at 1-2 MW; set a realistic bound for your facility size.
Schneider Electric 2018
Add battery catalogue parameters: chemistry, service life at 25°C, m² per kWh, kg per kWh and floor loading.
Schneider Electric 2017
Prefer Li-ion with a 10-year life as the default for edge and rack UPS.
Schneider Electric 2025
In the energy dashboard, show IT-side levers (utilization, accelerated computing) next to facility PUE.
U.S. DOE FEMP / NREL 2024
Weigh the supply air setpoint against server fan energy: raise it in small steps within the ASHRAE recommended range so the most demanding inlet nears 80 °F, only after air management is in place, and control to IT inlet temperature rather than return temperature.
BRE Global 2012
In existing-site assessments, show the legacy scheme when the user records a BREEAM DC 2010 certificate.
BRE Global 2019
Metering rule: if projected PUE is below 1.2 require IT-level (PUE3) metering; at 1.2-1.5 require at least PDU-output (PUE2); otherwise UPS-output (PUE1) is acceptable.
Schneider Electric 2024
Add an efficiency-degradation factor to the opex model for run-to-fail operation (+19%/+29%/+39%/+51% cooling energy in years 2 to 5) against the maintained case.
Schneider Electric 2017
Implement as the default heat-load calculator: Q = IT + (0.04 x UPS + 0.05 x IT) + (0.01 x UPS + 0.02 x IT) + 14.32 x area + 100 x people
Schneider Electric 2011
Use it as a quick-sizing calculator in novice mode: take IT kW, future kW, floor area, cooling type and UPS input type, and output service kW/A and generator kW, with the multipliers as editable defaults.
Schneider Electric 2019
Use as a seed for the TCO/capex comparison engine: liquidTechPremiumUsdPerW = 0.77 and chillerCrahSavingsUsdPerW = 0.91 (immersion).
European Commission (Official Journal of the European Union) 2024
Build the metering architecture to the regulation: meters on every supply input for total energy (grid and back-up generator separately) and at every UPS output for IT energy, with a system that retains measurement point and device records for at least 10 years.
All content and rights belong to the respective authors and publishers. SoSo CAD provides only the citation, its own summary and a link to the source, and is not responsible for the sources' content.