Topic guide

Energy

Discover publications on data centre energy consumption, power demand and efficiency. Investigate measurement methods, operating conditions and improvement approaches through summaries and original references.

Sources
416
Downloadable PDFs
122
Years
2007–2026

All sources

337–360 / 416

White paperPDF

Open Compute Project Foundation 2024

Data Center Facility Sustainability Metrics (OCP Data Center Facility white paper, October 2, 2024)

Build the metering plan so that PUE can be reported at the highest category possible, with IT load measured at PDU or equipment input rather than the UPS output where feasible.

  • External reporting is annual (required) and quarterly on a trailing 12 months (recommended); internal tracking should be continuous or monthly.
Technical guideCitation

Lawrence Berkeley National Laboratory (Center of Expertise for Energy Efficiency in Data Centers) / U.S. DOE FEMP 2020

Data Center Master List of Energy Efficiency Measures, Version 2.0 (September 2020)

Compare the planned UPS module count and redundancy scheme against the load curve: check the per-unit load at day-one and at full build, and consider modular units or switching off surplus modules.

  • Variable-speed chillers usually peak at 60-80% of full load; constant-speed chillers peak at full load.
Technical guideCitation

U.S. DOE Better Buildings / Lawrence Berkeley National Laboratory 2017

Data Center Metering and Resource Guide (February 2017)

At a stand-alone site, design meters that record energy (kWh) at the utility entrance and at the UPS output (or at panels serving only IT if there is no UPS); a UPS display that shows only power (kW) is not enough.

  • PUE Level 1 for a stand-alone data center is utility meter reading divided by UPS output energy (M1/M2).
Technical guidePDF

European Commission JRC 2020

Development of the EU Green Public Procurement (GPP) Criteria for Data Centres, Server Rooms and Cloud Services - Final Technical Report (JRC118558, EUR 30251 EN, 2020)

Ask in the specification for a designed PUE (dPUE) at a stated IT load (for example 50%) and conditions, under ISO/IEC 30134-2 or EN 50600-4-2, and write PUE demonstration at handover and the commissioning test into the contract.

  • ASHRAE liquid cooling classes cited: W1 2-17 °C, W2 2-27 °C, W3 2-32 °C, W4 2-45 °C, W5 above 45 °C.
White paperFree to read

Schneider Electric 2011

Economizer Modes of Data Center Cooling Systems

Compute economizer hours from hourly climate data (dry bulb and wet bulb) against the chosen supply setpoint and approach temperatures, and report partial and full economizer hours separately.

  • Cooling towers consume about 40 gpm per 1,000 tons of capacity (151.4 L/min).
White paperCitation

TÜV NORD Year not stated

EN 50600 white paper (TÜV NORD)

Point to this paper only as an orientation resource for newcomers to the EN 50600 family; do not derive calculation rules from it.

  • Related standards: EN 50600-1 and ISO/IEC 22237.
Technical guidePDF

U.S. EPA / ENERGY STAR 2024

ENERGY STAR Program Requirements for Computer Servers, Version 4.0 (Partner Commitments, Eligibility Criteria, and Final Test Method Rev. April 2023)

Write ENERGY STAR Version 4.0 certification and the PSU efficiency steps (at 10% to 100% load points) into the server procurement specification; look especially at 10% and 20% load efficiency for redundant supplies that run lightly loaded.

  • EffACTIVE = EXP(0.65 ln EffCPU + 0.30 ln EffMEMORY + 0.05 ln EffSTORAGE).
Technical guidePDF

U.S. EPA / ENERGY STAR 2017

ENERGY STAR Program Requirements for Uninterruptible Power Supplies (UPSs) - Partner Commitments, Eligibility Criteria Version 2.0, and Test Method (Rev. Dec-2017)

Write the Version 2.0 thresholds into UPS procurement as a floor; for VFI units above 10,000 W compute the minimum from 0.0058 x ln(P) + 0.886 for the actual rating.

  • Modular UPSs in the 1,500-10,000 W range receive an efficiency allowance (EMOD) of 0.004.
Technical guidePDF

European Commission, DG Communications Networks, Content and Technology (DG CONNECT) 2020

Energy-efficient Cloud Computing Technologies and Policies for an Eco-friendly Cloud Market: Final Study Report (SMART 2018/0028)

Use the regional and size-based values for first-pass PUE assumptions, but treat them as 2018-and-earlier averages and as historical context, not as a current target.

  • German PUE in 2015: 2.1 for server rooms under 100 m2, 1.9 for 100-500 m2, 1.7 for 500-5,000 m2, 1.6 above 5,000 m2.
Technical guideFree to read

NOAA National Centers for Environmental Information (NCEI) 2016

Global Surface Hourly / Integrated Surface Database (ISD), dataset C00532 - ISO 19115-2 metadata record

For cooling design use a station's hourly dry-bulb and wet-bulb (or dew point) data to count free-cooling and economiser hours in 1 degree C bins; SoSo CAD builds annual 1 degree C dry-bulb and wet-bulb hour bins for this purpose from one year of station files.

  • Over 14,000 active stations are updated daily; online data are typically delayed 24 hours.

All content and rights belong to the respective authors and publishers. SoSo CAD provides only the citation, its own summary and a link to the source, and is not responsible for the sources' content.