Topic guide

Sustainability

Browse publications on environmental impacts, carbon, resource use and life cycles. Compare assessment methods while reviewing their scope, data periods and reporting boundaries alongside the original sources.

Sources
201
Downloadable PDFs
66
Years
2007–2026

All sources

145–168 / 201

Technical guidePDF

European Commission JRC 2025

2025 Best Practice Guidelines for the EU Code of Conduct on Data Centre Energy Efficiency (JRC141521, EUR 40267)

Design the facility to operate within the ASHRAE Class A2 allowable range and require A2 operation within warranty in IT procurement; plan separate environmental zones (practice 5.3.4) for legacy equipment.

  • IT equipment AC/DC power converters should be rated at 90% efficiency or better across expected load ranges.
RegulationPDF

European Commission (Official Journal of the European Union) 2024

Commission Delegated Regulation (EU) 2024/1364 of 14 March 2024 on the first phase of the establishment of a common Union rating scheme for data centres

Build the metering architecture to the regulation: meters on every supply input for total energy (grid and back-up generator separately) and at every UPS output for IT energy, with a system that retains measurement point and device records for at least 10 years.

  • Data centre electricity demand is projected to reach 3.2% of total EU demand by 2030, a 28% increase over 2018.
White paperPDF

Open Compute Project Foundation 2024

Data Center Facility Sustainability Metrics (OCP Data Center Facility white paper, October 2, 2024)

Build the metering plan so that PUE can be reported at the highest category possible, with IT load measured at PDU or equipment input rather than the UPS output where feasible.

  • External reporting is annual (required) and quarterly on a trailing 12 months (recommended); internal tracking should be continuous or monthly.
Technical guidePDF

European Commission JRC 2020

Development of the EU Green Public Procurement (GPP) Criteria for Data Centres, Server Rooms and Cloud Services - Final Technical Report (JRC118558, EUR 30251 EN, 2020)

Ask in the specification for a designed PUE (dPUE) at a stated IT load (for example 50%) and conditions, under ISO/IEC 30134-2 or EN 50600-4-2, and write PUE demonstration at handover and the commissioning test into the contract.

  • ASHRAE liquid cooling classes cited: W1 2-17 °C, W2 2-27 °C, W3 2-32 °C, W4 2-45 °C, W5 above 45 °C.
Technical guidePDF

European Commission, DG Communications Networks, Content and Technology (DG CONNECT) 2020

Energy-efficient Cloud Computing Technologies and Policies for an Eco-friendly Cloud Market: Final Study Report (SMART 2018/0028)

Use the regional and size-based values for first-pass PUE assumptions, but treat them as 2018-and-earlier averages and as historical context, not as a current target.

  • German PUE in 2015: 2.1 for server rooms under 100 m2, 1.9 for 100-500 m2, 1.7 for 500-5,000 m2, 1.6 above 5,000 m2.

All content and rights belong to the respective authors and publishers. SoSo CAD provides only the citation, its own summary and a link to the source, and is not responsible for the sources' content.