Cummins 2017
Considerations when Paralleling Generating Sets
Check smallest-to-largest set ratio against the 30% guideline and flag designs below it.
- Waveform guidance: THD up to 5%, any single harmonic up to 3%.
Topic guide
Explore publications on data centre electrical infrastructure, from power distribution and protection to supply architectures and capacity planning. Compare technical summaries, publication details and links to the original references.
49–72 / 358
Cummins 2017
Check smallest-to-largest set ratio against the 30% guideline and flag designs below it.
Schneider Electric 2017
Distinguish 'N+1 internal modular', 'N+1 parallel redundant' and 'isolated redundant' instead of a single N+1 flag; for modular frames store module rating, max modules, shared battery bus and redundant controls/fans.
Eaton 2025
Add grid-code parameters to the utility connection object: UFLS stages, LVRT curve, post-fault power recovery ramp (%/s) and short-circuit ratio at the PCC.
Consulting-Specifying Engineer 2018
In business-model templates (enterprise, colo, cloud), set default redundancy and base-to-redundant ratios.
Cummins 2025
Give generator catalogue entries a rating table keyed by class {ESP, PRP, COP, DCP, DCC/manufacturer-unlimited} rather than a single kW value.
Cushman & Wakefield 2026
In the cost module, offer an all-in $/MW benchmark band with source and year and allow a market multiplier.
Lawrence Berkeley National Laboratory, Center of Expertise for Energy Efficiency in Data Centers 2023
Benchmark the electrical loss model against this tool's structure: transformer, UPS and PDU efficiency curves by load factor, plus eco-mode.
Open Compute Project Foundation 2025
Rack catalogue entries should carry a distribution-voltage attribute (48 VDC, +/-400 VDC, AC); flag 48 V in-rack designs above roughly 150 kW per rack as needing a sidecar or higher-voltage DC architecture.
Open Compute Project Foundation 2026
Choose the voltage class with LV limited to 1500 VDC; check that sources stay below it in steady state (for example 750 V per pole) and that device voltage windows fit; 800 V devices with only a +/-5% range cannot operate below 750 V and are unusable there.
arXiv preprint (University College Dublin) 2025
Expose UPS transfer thresholds (voltage %, frequency Hz), return-to-mains delay and staggering across UPS modules as design parameters, and warn when all modules share identical thresholds and delays, since synchronised reconnection can re-trip the grid.
Consulting-Specifying Engineer 2013
Offer distribution-voltage options (208/120, 415/240, 380 Vdc) with automatic loss and fault-current comparison.
Aksa Power Generation 2020
Keep both standby and DCC kVA per model in the generator catalog; where data is missing, use DCC ~0.9-0.94 x standby as a flagged estimate.
Huawei Digital Power 2022
Add a 'prefabricated power train' block type (transformer, LV, UPS, feeders) carrying footprint, weight and a clearance envelope.
Schneider Electric 2012
Store reference designs as structured objects with required attribute fields (IT kW range, redundancy N/N+1/2N for power and cooling, density kW/rack, annualized PUE, heat rejection type, estimated cost) plus linked one-lines, layouts and BOM lines (part number, qty, supplier).
Schneider Electric 2012
Capture the IT load profile at project setup as four fields (initial kW, minimum final kW, maximum final kW, ramp-up years, default lifetime 10 years), not one design load.
Danfoss 2026
In the cooling-plant builder keep a component list per subsystem (chiller, CDU, pump skid, heat recovery) with fields for maximum chilled-water temperature, HX approach temperature and VFD THDi.
Eaton 2013
Allow UPS placement in the white space with an airflow-pattern attribute (front-to-back, front-to-top) and count its heat release in the hall cooling load.
Legrand 2022
Give UPS records an architecture enum {conventional, modular, scalable_modular}, module rating, maximum parallel units, MTTR hours and a hot-swap flag; store efficiency at 25/50/75/100% load, not one number.
ABB 2022
Use it as a template for a '2N LV, 0.5 MW' starter project, auto-generating the RPDU, RPP, secondary board, UPS, main board and transformer/generator chain from rack count and kW/rack.
Socomec 2024
In the single-line editor, tag transfer devices as ATSE (IEC 60947-6-1) or STS with a transfer-time field, and suggest STS where the load needs under about 10 ms.
IEEE Open Journal of Industry Applications (Institute of Electrical and Electronics Engineers (IEEE)) 2024
For UPS battery arc-flash checks at 380-1000 VDC, expect incident energy to rise sharply with voltage and arc duration above roughly 500-800 V.
Caterpillar 2014
Store per rating the kW, average-load-factor limit, annual-hour limit, overload allowance and a utility-paralleling-permitted flag.
Uptime Institute Journal (Uptime Institute) 2025
Define AI rack presets at about 130, 85, 50, 26 and under 20 kW, each with its liquid versus air cooling split.
Springer Science and Business Media LLC (preprint) 2026
Make the 0.1-10 Hz oscillation, 1.40 peak-to-mean ratio and coincidence factor explicit inputs in the AI campus load model, and check storage and buffering against grid ramp limits.