Browse references on airflow management, aisle arrangements and rack inlet conditions. Investigate cooling distribution and air mixing alongside the measurement methods and modelling assumptions reported by each source.

Sources
118
Downloadable PDFs
37
Years
2008–2026

All sources

73–96 / 118

Research paperCitation

Energy and Buildings (Elsevier) 2021

Prototype energy models for data centers

Use the prototype densities and the approach-temperature concept to calibrate the tool's hourly cooling model and containment effectiveness.

  • The models follow ASHRAE 90.1 minimum requirements across vintages.
Research paperPDF

Sustainability (MDPI AG) 2026

Retrofit Optimization of Raised-Floor Plenum Thermal Performance for Energy-Efficient and Sustainable Operation of Non-Standard Campus Data Centers

For plenum imbalance, consider a 50%-perforated transverse baffle about 0.3 m from the unit outlet; 50% open gave a smaller resistance increase than 30% (8.5% against 18.7%).

  • For S4, SHI fell from 0.42 to 0.35, maximum rack inlet temperature fell from 27.2 °C to 26.7 °C, and all racks met the 27 °C ASHRAE recommended limit.
Research paperFree to read

Swiss Federal Office of Energy SFOE (Energy Research and Cleantech); preprint on arXiv 2025

Temperature Optimisation in Data Centres (TODC) - Final report

Add an IT-side penalty of about 0.3-0.6% of IT power per C of inlet rise above about 23 C (a configurable default) to the setpoint optimiser and energy calculator, and model fan power with the cube of speed.

  • Reported hyperscale inlet temperatures: Google 26.6 C, Microsoft 27 C, Meta 29.4 C.
White paperFree to read

Schneider Electric 2015

Ten Cooling Solutions to Support High-density Servers

Set density warnings by air-distribution type: uncontained flooded return above 3 kW/rack average, uncontained raised floor above 3-6 kW/rack, fan-assisted retrofit ceiling 8 kW/rack, HACS/RACS pods up to 60 kW/rack.

  • Fan-assisted devices raise rack cooling to 3-8 kW and should be UPS-powered.
White paperFree to read

Schneider Electric 2017

The Use of Ceiling-Ducted Air Containment in Data Centers

Add passive and active ducted racks and ducted HACS to the containment selector, with density limits tied to a ceiling plenum vacuum input (default 0.03 inH2O / 7.5 Pa, warning above 0.06 inH2O / 15 Pa).

  • Cooling-to-IT airflow ratio: 1 for HACS, 1.2 or higher for ducted racks.
Research paperPDF

Buildings (MDPI AG) 2026

Thermal Environment Assessment for Energy-Efficient Cooling in Air-Cooled Data Centers: Measurement, CFD, and Predictive Models

In a design tool, set CFD accuracy expectations from this review's ranges (0.1-4 °C absolute, relative mostly below 20%) and do not limit validation scope to temperature; ask for velocity and pressure too.

  • Of the 58 CFD studies, Fluent was used in 24 (41.4%) and 6SigmaDC in 12; standard k-epsilon in 41 (about 70.7%).
Research paperPDF

arXiv preprint (Nanyang Technological University / NVIDIA AI Technology Center) 2025

Transforming Future Data Center Operations and Management via Physical AI

For fast what-if analysis consider a CFD-trained surrogate (inference about 0.01 s), but state that the surrogate is only as accurate as the CFD it was trained on and is not validated against measurements.

  • The CapEx of building a data centre with 100k B200 GPUs is 4.5 to 5 billion US dollars and annual electricity OpEx can reach 400 million.
Technical guideFree to read

TMMOB Makina Mühendisleri Odası (MMO) 2025

Testing-adjusting-balancing of data centres

In the commissioning module, include a TAB task list per cooling unit and hydronic circuit (design versus measured airflow, water flow, differential pressure, set points).

  • The reported outcome is a 10-25% energy efficiency improvement.
White paperFree to read

Rittal 2017

Whitepaper Rittal Liquid Cooling Packages

Catalogue close-coupled coolers by type (inline row, closed-loop rack, rear door, DX rack), rated kW, width, footprint, maximum air delta-T and water/refrigerant inlet temperatures.

  • Hybrid doors come in 10 kW and 20 kW versions and open 130 degrees.

All content and rights belong to the respective authors and publishers. SoSo CAD provides only the citation, its own summary and a link to the source, and is not responsible for the sources' content.