Air-Assisted Direct Liquid Cooling: An Overlooked Option
Offer a 'liquid-to-air CDU / sidecar' as a DLC option.
- Published as UII Update 233 in Q1 2024.
Topic guide
Explore technical publications on data centre cooling systems, thermal loads and operating conditions. Review air and liquid approaches, energy use and operational requirements within each source’s scope.
25–48 / 339
Uptime Institute Intelligence 2024
Offer a 'liquid-to-air CDU / sidecar' as a DLC option.
Upsite Technologies blog 2017
Include server fan power rising with inlet temperature in the cooling energy tool (for example about +13% from 68 to 104 F for A3) so set-point optimisation minimises total energy, not PUE.
Energies (MDPI AG) 2018
In airside economiser design, plan exhaust grilles and the building envelope so recirculation stays below 5%; 15% recirculation raised energy about 6.1% for direct and 9% for indirect.
Vertiv 2016
Add a pumped-refrigerant economizer DX type to the cooling-option library, with economizer hours modelled as a function of ambient, load fraction and return-air temperature.
ASHRAE 2020
In the CRAC catalogue, record rated capacity and efficiency (NSenCOP) on the basis of AHRI 1360 / ASHRAE 127 test conditions.
ASHRAE 2022
In the compliance calculator, compute annualised MLC and design ELC per segment (UPS, distribution, PDU) and compare them with climate-zone limits.
BICSI (via Cabling Installation & Maintenance) 2019
Keep BICSI 002 edition history (2014, 2019, 2024) in the standards registry for projects citing older editions.
Telecommunications Industry Association (TIA) 2024
Offer a rating-level selector (Rated-1..4) that is separate from Uptime Tiers.
Energies (MDPI AG) 2023
For an operational thermal twin, define adequate sensor density covering supply, return, cold-aisle and hot-aisle temperatures and equipment power (728 points at 15-minute sampling in this study).
ASHRAE 2024
Use Book 2 (IT Equipment Power Trends) for default kW-per-rack growth projections.
ASHRAE 2024
Do not hard-code A2 as the minimum class; allow H1/A1 classes for AI racks.
Consulting-Specifying Engineer 2019
Implement the 90.4 MLC and ELC calculators with the correct test load points per UPS redundancy class (N/N+1 vs 2N).
Schneider Electric 2011
In layout validation, raise an error when adjacent rows of front-to-back equipment face the same direction, and a warning for perforated tiles or supply diffusers in a hot aisle.
Schneider Electric 2012
In the capacity planner keep design, installed and expected-load curves separate per phase and show utilisation over a 10-year horizon; default start-up load to 20-30% of design and final load to 60-90%.
Open Compute Project Foundation 2022
Use the summary table as validation rules for immersion-fluid catalogue entries: flash point, pour point, viscosity, density and dielectric properties.
Open Compute Project Foundation 2026
Record ASHRAE 34 safety class, GWP, ODP, boiling point and latent heat in the two-phase cold-plate fluid catalogue.
TMMOB Makina Mühendisleri Odası (MMO) 2023
In the energy module, when on-site CHP/trigeneration is modelled, report PUE together with source-aware metrics (primary energy, CO2 and optionally exergy-based figures).
BICSI 2026
Add a 'credentials' field to the user profile and recognise DCDC as a value there.
T.C. Cumhurbaşkanlığı Siber Güvenlik Başkanlığı 2026
Provide a Turkey public-sector compliance checklist mapping the measures to design objects: dedicated IT UPS, N+1 air conditioning with auto changeover, redundant feeds, generator fuel redundancy, room adjacency checks against wet areas.
Journal of Engineering Research and Sciences (Journal of Engineering Research and Sciences) 2026
Do thermal verification of failure mode (two ACUs offline) with realistic air leakage (cabinet gaps, HAC panel joints); a leak-free model can comply while the leaky model exceeds 32 °C.
Schneider Electric 2014
Capture peak kW/rack and the peak-to-average ratio as well as the average, and express density in W/rack instead of W/m2.
Resources, Conservation and Recycling (Elsevier BV) 2022
In early data-centre design, set PUE and WUE targets by size class, cooling system and climate zone using this study's ranges (for example 1.71-2.22 for small rooms, 1.12-1.25 for large scale).
Uptime Institute Journal 2014
For in-row and RDHx designs, evaluate cooling redundancy per aisle or row, not per room, and check unit throw distance to the farthest rack under N-1.
European Commission 2021
Add an "EU Taxonomy 8.1" compliance profile: a Code of Conduct expected-practice checklist with justification fields for non-applicable items, and a refrigerant GWP <= 675 check in the cooling catalogue.