Topic guide

Cooling

Explore technical publications on data centre cooling systems, thermal loads and operating conditions. Review air and liquid approaches, energy use and operational requirements within each source’s scope.

Sources
339
Downloadable PDFs
92
Years
2006–2026

All sources

73–96 / 339

Technical guideFree to read

Danfoss 2026

Data center solutions powering the digital economy

In the cooling-plant builder keep a component list per subsystem (chiller, CDU, pump skid, heat recovery) with fields for maximum chilled-water temperature, HX approach temperature and VFD THDi.

  • Advanced Active Filter with SiC switches quoted at 98.2% efficiency.
White paperPDF

Open Compute Project Foundation 2023

Data Centers Heat Reuse 101

A heat-reuse module should report recoverable heat (kW) and its temperature band by cooling technology (air, RDHx, DLC/immersion) and suggest compatible heat-host categories.

  • Containerised/modular data centres can exceed 0.5 MW, a significant heat quantity for many local applications.
Research paperPDF

npj Clean Water (Springer Science and Business Media LLC) 2021

Data centre water consumption

In cooling selection, add the roughly 25.5 million litres per year per MW of evaporative cooling water need and the potable share (57-65%) to the siting and water supply decision.

  • Raising chilled-water temperature from the usual 7-10 °C to 18-20 °C can cut expenses by 40%.
Research paperPDF

Frontiers in Energy Research (Frontiers Media SA) 2022

Discussions of Cold Plate Liquid Cooling Technology and Its Applications in Data Center Thermal Management

For loads of 50 kW per rack and above, evaluate a hybrid cold-plate scheme (main loads on cold plates, remaining heat in air) for a PUE target below 1.2.

  • Cabinets with enclosed water-cooled backplanes can save nearly 35% of annual energy compared with air-cooled backplanes.
Technical guideFree to read

Open Compute Project Foundation 2025

Door Heat Exchanger Sub-Project Updates (OCP EMEA Summit 2025)

Record approach temperature difference, P-Q curve, fan/pump redundancy and coil material in rear-door and sidecar catalogue items.

  • Sidecars should align with ORv3 dimensions using Single Rack Space units; pumps and fans redundant and hot-swappable, heat exchanger treated as a single point of failure.
Technical guideFree to read

Consulting-Specifying Engineer 2015

Driving data center PUE, efficiency

Include economizer control limits, part-load loss curves for each electrical stage and the redundancy topology as energy model inputs.

  • Water-cooled IT still rejects roughly 10-30% of cabinet capacity to air; such cabinets typically house 50-80 kW.
Research paperPDF

Frontiers in Built Environment (Frontiers Media SA) 2024

Effects and optimization of airflow on the thermal environment in a data center

Make aisle containment the default in raised-floor or in-row cooling: containment raised ASE from 65.69% to 85.57-90.25% and brought SHI close to zero.

  • Without containment, cabinet No. 19 had a mean inlet temperature of 30.1 °C and a maximum of 36.7 °C, and ten cabinets went above the 27 °C limit.
Research paperPDF

Sustainability (MDPI AG) 2023

Energy Consumption and Energy Saving Analysis of Air-Conditioning Systems of Data Centers in Typical Cities in China

Show evaporative free-cooling feasibility with a potential-hours study that bins the city's hourly wet-bulb distribution against mode thresholds (13 and 15 °C); in a humid climate direct evaporative mode ran only 262 h a year.

  • The air-system retrofit gave PUE below 1.39 everywhere; the best case was Xinjiang, 1.62 to 1.18 (69.26%).
Research paperPDF

Scientific Reports (Springer Science and Business Media LLC) 2025

Energy efficiency enhancement in two European data centers through CFD modeling

Set up the retrofit workflow as KPI-guided: with a validated CFD model compute RCI, RHI, RTI and the recirculation index, then test rack repositioning, separators, sealing unused bays and removing badly placed ventilation units in sequence.

  • KPI limits: ASHRAE recommended 18-27 °C and allowable 15-32 °C inlet temperatures.
Research paperPDF

Energies (MDPI AG) 2025

Energy Efficiency Measurement Method and Thermal Environment in Data Centers—A Literature Review

In PUE comparisons state the facility type (edge, SMB, enterprise, colocation, hyperscale) and assign IT/facility power categories per The Green Grid definitions in detail; PUE across types is not directly comparable.

  • No study of staff thermal comfort in data centres was found; in one computer lab PMV was 1.1-1.4, outside the ISO ±0.5 band.