Topic guide

Reliability

Explore references on reliability, availability and redundant architectures. Review failure models, maintenance arrangements and system dependencies while keeping the evidence, methods and scope of each publication in view.

Sources
255
Downloadable PDFs
58
Years
2002–2026

All sources

121–144 / 255

Research paperPDF

Fire (MDPI AG) 2026

Reframing Data Center Fire Safety as a Socio-Technical Reliability System: A Systematic Review

Ask for a fire-safety design file that covers a lifecycle plan (aligned with NFPA 75 and NFPA 76) including emergency response, damage control and post-fire recovery, not only prevention and suppression.

  • The search found 806 records (Scopus 330, Web of Science 476); twelve empirical studies were synthesised and benchmarked against NFPA 75 and NFPA 76.
Research paperFree to read

Proceedings of the 2018 3rd Joint International Information Technology,Mechanical and Electronic Engineering Conference (JIMEC 2018) (Atlantis Press) 2018

Research on Availability of Data Center UPS Power Supply System

Offer 'UPS + utility (mains) dual bus' as a topology template beside 2N and N+1, with an RBD calculation that shows it can match 2N for dual-corded IT load.

  • Power-system failures are cited as 72.2% of data-centre failures.
Research paperPDF

World Electric Vehicle Journal (MDPI AG) 2023

Research on Calendar Aging for Lithium-Ion Batteries Used in Uninterruptible Power Supply System Based on Particle Filtering

Plan UPS battery replacement from the RUL of the weakest cell rather than the string average; in a series string one cell sets the replacement date for the whole string even when others have years of life left.

  • Per-cell SOH estimation RMSE ranged from 0.15% to 9.07% (MAPE 0.16% to 6.85%).
Technical guideFree to read

Eaton 2008

Selective Coordination (Cooper Bussmann Electrical Protection Handbook section)

In the coordination checker store device type (fuse class, breaker with or without instantaneous, STD band) and use ratio tables or tested pair tables rather than curves when fault current puts both devices below 0.01 s.

  • Fuse selectivity: load-side total clearing I2t below line-side melting I2t; Low-Peak families need 2:1 amp ratio, other combinations up to 8:1.
Research paperFree to read

Revista de Informática Teórica e Aplicada (Universidade Federal do Rio Grande do Sul) 2019

Stochastic Models for Optimizing Availability, Cost and Sustainability of Data Center Power Architectures through Genetic Algorithm

Recognise that topology choice is only part of availability; equipment selection within a fixed topology can trade availability, losses and cost.

  • Tier I: cost 122,322.20 to 116,004.52 USD (5.16%), exergy 203.39 to 140.13 J (31.10%), availability 3.3643 to 3.4005 nines.
Technical guideFree to read

Data Center Frontier (Black & Veatch contributed article) 2024

The Benefits of Implementing Substations for Data Centers

Offer a substation object with a configuration field (radial, main-tie-main, ring bus, breaker-and-a-half, double-bus double-breaker) and an insulation type field (AIS, GIS), with footprint and cost multipliers.

  • Some high-voltage equipment has 1-3 year procurement lead times.
Research paperPDF

Energies (MDPI AG) 2017

Thermal Impact Analysis of Circulating Current in High Power Modular Online Uninterruptible Power Supplies Application

For paralleled modules in a modular UPS, do not look only at the N+1 redundancy count; add to the design check that module-to-module filter and control parameter differences cause circulating current and thermal imbalance.

  • The authors recommend keeping overshoot or sag on module switching within 10% of nominal critical-bus voltage.