Find references on fire detection, suppression and data centre fire safety. Implementation requires the original publication, project conditions and assessment by the responsible qualified specialists.

Sources
56
Downloadable PDFs
20
Years
2007–2026

All sources

25–48 / 56

Research paperPDF

Fire (MDPI AG) 2026

Probabilistic Risk Assessment of Grid-Scale Lithium-Ion Battery Energy Storage System Fire Hazards: Hydrogen Fluoride (HF) Toxicity, Suppression Effectiveness, and Comparative Compartment Design Analysis

Compare BESS compartmentation quantitatively: two compartments halve HF dose and IDLH clearance time, but IDLH is still exceeded for anyone in the room in full thermal runaway, so runaway prevention (BMS integrity, UL 9540A containment, emergency power off) must stay the primary control.

  • Mean IDLH (25 mg/m³) clearance time with 9 ACH was 599 min for one compartment and 301 min for two; the probability of clearing within 5 min was 0% for both.
Research paperPDF

Fire (MDPI AG) 2026

Reframing Data Center Fire Safety as a Socio-Technical Reliability System: A Systematic Review

Ask for a fire-safety design file that covers a lifecycle plan (aligned with NFPA 75 and NFPA 76) including emergency response, damage control and post-fire recovery, not only prevention and suppression.

  • The search found 806 records (Scopus 330, Web of Science 476); twelve empirical studies were synthesised and benchmarked against NFPA 75 and NFPA 76.
Research paperPDF

Fire (MDPI AG) 2023

Simulation Test on Cooling and Fire Suppression with Liquid Nitrogen in Computer Room of Data Center

When assessing non-gas, non-water suppression options, note liquid nitrogen only as a preliminary-stage option, and ask for full-scale testing and an occupant-safety analysis for oxygen depletion before taking design values.

  • Liquid nitrogen extinguished the optical-fibre fire within 3 min and the UPS-component fire within 2 min.
Technical guideFree to read

TMMOB Makina Mühendisleri Odası (MMO) 2019

Fire extinguishing system functions and integration with other engineering disciplines (Söndürme Sistemleri Fonksiyonları, Diğer Mühendislik Disiplinleri ile Entegrasyonu)

When a room uses gaseous suppression, require HVAC damper/fan shutdown interlocks, a pressure-relief vent and a 10-minute hold-time integrity test in the commissioning list.

  • For clean-agent rooms, the minimum extinguishing concentration should be held for at least 10 minutes, verified by room integrity testing.
Research paperPDF

IEEE Open Journal of Industry Applications (Institute of Electrical and Electronics Engineers (IEEE)) 2025

Study of DC Arc Flash Phenomenon From 1000 V Lithium Ion Battery Systems

In arc flash estimation for high-voltage battery rooms, do not use the maximum-power method alone with an enclosure multiplier; cross-check unrealistic results with measurement-based models such as Ammerman's.

  • 91 arc-flash experiments were performed on LFP and LTO lithium-ion battery sources at voltages up to roughly 1000 VDC.
Technical guideFree to read

Consulting-Specifying Engineer 2017

Demystifying IT room protection requirements

If containment roofs or chimneys are placed, require sprinkler heads below or inside the containment, or fusible-link drop-away panels.

  • Gaseous systems must be automatically actuated by NFPA 72-compliant detection.