Topic guide

Cooling

Explore technical publications on data centre cooling systems, thermal loads and operating conditions. Review air and liquid approaches, energy use and operational requirements within each source’s scope.

Sources
339
Downloadable PDFs
92
Years
2006–2026

All sources

193–216 / 339

White paperFree to read

Schneider Electric 2015

Ten Cooling Solutions to Support High-density Servers

Set density warnings by air-distribution type: uncontained flooded return above 3 kW/rack average, uncontained raised floor above 3-6 kW/rack, fan-assisted retrofit ceiling 8 kW/rack, HACS/RACS pods up to 60 kW/rack.

  • Fan-assisted devices raise rack cooling to 3-8 kW and should be UPS-powered.
White paperFree to read

Schneider Electric 2017

The Use of Ceiling-Ducted Air Containment in Data Centers

Add passive and active ducted racks and ducted HACS to the containment selector, with density limits tied to a ceiling plenum vacuum input (default 0.03 inH2O / 7.5 Pa, warning above 0.06 inH2O / 15 Pa).

  • Cooling-to-IT airflow ratio: 1 for HACS, 1.2 or higher for ducted racks.
Research paperPDF

Sustainability (MDPI AG) 2015

The Water Footprint of Data Centers

Compare HVAC options not only by on-site water use but by total water footprint including the grid's water intensity (WUEsource); the ranking can flip with the grid.

  • Outbound data traffic carries a water footprint of 1-205 litres per gigabyte; the high end is close to the 214 L footprint of 1 kg of tomatoes.
Research paperPDF

Buildings (MDPI AG) 2026

Thermal Environment Assessment for Energy-Efficient Cooling in Air-Cooled Data Centers: Measurement, CFD, and Predictive Models

In a design tool, set CFD accuracy expectations from this review's ranges (0.1-4 °C absolute, relative mostly below 20%) and do not limit validation scope to temperature; ask for velocity and pressure too.

  • Of the 58 CFD studies, Fluent was used in 24 (41.4%) and 6SigmaDC in 12; standard k-epsilon in 41 (about 70.7%).
Technical guideCitation

Trane Technologies / UL Environment 2023

Trane Centrifugal Chillers EPD 4790566295.101.1

In preliminary embodied-carbon calculations, use 129 kg CO2e per refrigeration ton as a proxy factor for water-cooled centrifugal chillers and label it as a proxy.

  • The source value is on page 14, Table 18; the declared unit is on page 2.
Research paperPDF

arXiv preprint (Nanyang Technological University / NVIDIA AI Technology Center) 2025

Transforming Future Data Center Operations and Management via Physical AI

For fast what-if analysis consider a CFD-trained surrogate (inference about 0.01 s), but state that the surrogate is only as accurate as the CFD it was trained on and is not validated against measurements.

  • The CapEx of building a data centre with 100k B200 GPUs is 4.5 to 5 billion US dollars and annual electricity OpEx can reach 400 million.
Technical guideFree to read

Open Compute Project Foundation 2025

Unraveling the Efficiency, Performance and Sustainability Trade-Offs: Case Study of Liquid Assisted Air Cooling vs Traditional Air Cooling (OCP EMEA Summit 2025)

Distinguish LAAC (no facility water, heat still rejected to room air) from DLC with facility water in the server catalog, and do not reduce air-side cooling load for LAAC racks.

  • CPU, NIC and DC-SCM were cooler; DIMMs ran 3-6 C hotter and SSD/PSU temperatures rose.

All content and rights belong to the respective authors and publishers. SoSo CAD provides only the citation, its own summary and a link to the source, and is not responsible for the sources' content.