Topic guide

Racks

Explore sources on rack layouts, power density and IT equipment interfaces. Review technical notes to understand how mechanical, electrical and cooling requirements meet at the rack level.

Sources
191
Downloadable PDFs
52
Years
2008–2026

All sources

97–120 / 191

Technical guidePDF

Open Compute Project Foundation 2022

Reservoir and Pumping Unit (RPU) Specification, Ver 1.0

Model AALC (RPU plus door or rack liquid-to-air heat exchanger) as a cooling option for air-cooled halls, counting the RPU's 4RU space, 75 kg mass and the 2%/5% parasitic power caps against rack U-space, weight and power budgets.

  • AALC total power is at most 5% of rated cooling capacity, of which the RPU takes at most 40%.
Research paperPDF

IEEE Access (Institute of Electrical and Electronics Engineers (IEEE)) 2026

Review of the 800-VDC Power Delivery Architecture and Isolated 800-V to 48-V Converter Solutions for Future AI Data Centers

Define 800 VDC unipolar, ±400 VDC bipolar and 48/54 VDC busbar as separate voltage classes in the single-line diagram, each with its own conductor ampacity, breaker pole count and clearance (IEC 60664-1) checks.

  • The OCP Open Rack V3 PSU specification targets above 97.5% peak efficiency and at least 96.5% across 30%-100% load.
Research paperFree to read

arXiv preprint (cs.DC) 2024

SCARIF: Towards Carbon Modeling of Cloud Servers with Accelerators

Add an embodied-carbon estimator per server SKU using the SCARIF linear model (5.01 kg per CPU core, 0.16 kg/GB SSD, 0.04 kg/GB HDD, 0.95 kg/GB DRAM, 83.08 kg x (year-2000), intercept -1100), and tag the result as an approximate, vendor-calibrated value.

  • Total embodied carbon of the highest/lowest servers: Dell 1782/1133, HP 3880/423, Lenovo 15593/585 kgCO2e.
White paperFree to read

Schneider Electric 2019

Solving Edge Computing Infrastructure Challenges

Provide an edge/micro data centre template: single-rack bundle of rack, UPS, rack PDU, cooling (passive default), sensors and cameras.

  • Prefabricated modules save about 50% of design and engineering time (WP 163).
Research paperPDF

IEEE Open Journal of Power Electronics (Institute of Electrical and Electronics Engineers (IEEE)) 2026

State-of-the-Art Power Electronics in AI Data Centers

In rack power templates, model PSU count per shelf and the 33 kW shelf limit for AC distribution, and check busbar, PDU and cooling impact together for racks that exceed 100 kW with several shelves.

  • AI rack density is 30-100+ kW against 7-10 kW for traditional racks; an 8-GPU DGX H100 draws around 10,200 W.
Research paperFree to read

arXiv preprint (Microsoft Azure Research / University of Illinois) 2025

TAPAS: Thermal- and Power-Aware Scheduling for LLM Inference in Cloud Platforms

Couple thermal and power headroom in the design tool: show how inlet temperature rise with outdoor conditions (for economiser or adiabatic systems) erodes GPU thermal margin and can trigger throttling.

  • GPU temperature must stay below a threshold (for example 85 C) beyond which hardware throttles computation.
Research paperFree to read

Swiss Federal Office of Energy SFOE (Energy Research and Cleantech); preprint on arXiv 2025

Temperature Optimisation in Data Centres (TODC) - Final report

Add an IT-side penalty of about 0.3-0.6% of IT power per C of inlet rise above about 23 C (a configurable default) to the setpoint optimiser and energy calculator, and model fan power with the cube of speed.

  • Reported hyperscale inlet temperatures: Google 26.6 C, Microsoft 27 C, Meta 29.4 C.
White paperFree to read

Schneider Electric 2015

Ten Cooling Solutions to Support High-density Servers

Set density warnings by air-distribution type: uncontained flooded return above 3 kW/rack average, uncontained raised floor above 3-6 kW/rack, fan-assisted retrofit ceiling 8 kW/rack, HACS/RACS pods up to 60 kW/rack.

  • Fan-assisted devices raise rack cooling to 3-8 kW and should be UPS-powered.
Research paperFree to read

ACM SIGEnergy Energy Informatics Review (Association for Computing Machinery (ACM)) 2023

The Dirty Secret of SSDs: Embodied Carbon

In the storage catalogue, store embodied carbon per drive SKU: a default of 0.16 kgCO2e/GB for SSD (Tannu and Nair SEF) and a much lower HDD default.

  • Server emissions are concentrated in the operational phase, whereas about 80% of an iPhone's emissions come from manufacturing.
White paperFree to read

Schneider Electric 2017

The Use of Ceiling-Ducted Air Containment in Data Centers

Add passive and active ducted racks and ducted HACS to the containment selector, with density limits tied to a ceiling plenum vacuum input (default 0.03 inH2O / 7.5 Pa, warning above 0.06 inH2O / 15 Pa).

  • Cooling-to-IT airflow ratio: 1 for HACS, 1.2 or higher for ducted racks.

All content and rights belong to the respective authors and publishers. SoSo CAD provides only the citation, its own summary and a link to the source, and is not responsible for the sources' content.