Topic guide

Site planning

Review publications on site selection, building layouts and the physical arrangement of data centre infrastructure. Explore capacity, environmental conditions, access and expansion in the context of your project.

Sources
147
Downloadable PDFs
36
Years
2001–2026

All sources

121–144 / 147

Technical guidePDF

Open Compute Project Foundation 2026

Interface Specification Between Hyperscalers and Utility Grid for Disturbance Performance (Version 1.0.0)

For a new site, write the POI LVRT/HVRT envelope and the PFAPR requirement (90% within 2 s) as design criteria, and settle which voltage measurement (line-to-neutral or line-to-line) governs during protection coordination with the utility.

  • In ERCOT NOGRR 282, cooling load is subtracted from the pre-fault load used to judge PFAPR.
Technical guideFree to read

Consulting-Specifying Engineer 2017

Demystifying IT room protection requirements

If containment roofs or chimneys are placed, require sprinkler heads below or inside the containment, or fusible-link drop-away panels.

  • Gaseous systems must be automatically actuated by NFPA 72-compliant detection.
Technical guideFree to read

NOAA National Centers for Environmental Information (NCEI) 2016

Global Surface Hourly / Integrated Surface Database (ISD), dataset C00532 - ISO 19115-2 metadata record

For cooling design use a station's hourly dry-bulb and wet-bulb (or dew point) data to count free-cooling and economiser hours in 1 degree C bins; SoSo CAD builds annual 1 degree C dry-bulb and wet-bulb hour bins for this purpose from one year of station files.

  • Over 14,000 active stations are updated daily; online data are typically delayed 24 hours.
Technical guidePDF

U.S. DoD (UFC) 2019

UFC 3-550-01 Exterior Electrical Power Distribution (1 September 2016, Change 3, 01 November 2019)

Settle the loop or alternate-feed arrangement and the maintenance isolation points for the MV run from utility entry to the building early; the text treats shortening maintenance outages as a direct design driver.

  • Elbow-type arresters go at the ends of all radials and at normally open loop points, for all voltages above 5 kV.

All content and rights belong to the respective authors and publishers. SoSo CAD provides only the citation, its own summary and a link to the source, and is not responsible for the sources' content.

Monthly newsletter · free

Keep your reading list current

Once a month: new library sources, changes to Turkish regulations and upcoming data centre events.